Good evening everyone,
I've managed to snag a job at a small store that requires a ton of dedicated circuits, and I'm planning on running pipe for it.
Only issue I'm having is I'm doubting my derating calculation.
Using table 2 for 12AWG under the 75° column I get 25 amps.
Using table 5c for 7-24 conductors in a pipe it's a derating factor of .7
25×.7 = 17.5 amps.
So if this math is right, then that means I can run up to 24 conductors through a pipe with 15 amp over current protection?
We don't do a lot of commercial work, we're mainly residential. I just want to make sure I won't get a defect for this. I could have asked the boss, but I forgot to when I seen him today.
Other question I have is, can I install an isolated ground outlet, and just run the isolated ground the the ground bus in the panel of the store? I'm wondering if it's okay to do it this way. (The boss has never had to install an isolated ground receptical... changed/replaced yes just not new lines). I'm just worried about interference or whatever for the cash register area (job is T&M so not worried about the extra cost to do it) or am I just over thinking this?
Edit: Maybe I should have posted this in the Canadian forum... oh well. It's general to me.
Sent from my SM-G920W8 using Tapatalk
I've managed to snag a job at a small store that requires a ton of dedicated circuits, and I'm planning on running pipe for it.
Only issue I'm having is I'm doubting my derating calculation.
Using table 2 for 12AWG under the 75° column I get 25 amps.
Using table 5c for 7-24 conductors in a pipe it's a derating factor of .7
25×.7 = 17.5 amps.
So if this math is right, then that means I can run up to 24 conductors through a pipe with 15 amp over current protection?
We don't do a lot of commercial work, we're mainly residential. I just want to make sure I won't get a defect for this. I could have asked the boss, but I forgot to when I seen him today.
Other question I have is, can I install an isolated ground outlet, and just run the isolated ground the the ground bus in the panel of the store? I'm wondering if it's okay to do it this way. (The boss has never had to install an isolated ground receptical... changed/replaced yes just not new lines). I'm just worried about interference or whatever for the cash register area (job is T&M so not worried about the extra cost to do it) or am I just over thinking this?
Edit: Maybe I should have posted this in the Canadian forum... oh well. It's general to me.